I disagree with this statement. There are rules for how far you need to be from a bend in the ductwork, rules for when a sampling tube needs to be supported inside the ductwork, how close they need to be from a rated wall, and we haven't talked about installing a duct smoke detector on a round section of duct or passing a magnahelic test. Accessibility is an issue since filters and the detectors themselves will need to be maintained.
Should contract documents specify that the EC installs the duct detectors, look for language in said documents to see who is responsible for WHERE the duct detector gets installed. This way, the EC isn't holding the bag if the duct detector won't pass a magnihelic test.