My electrical contractor is providing the duct smoke detector as it is in their contract. The contract drawing includes a duct smoke detector but did not indicate its location. The building is a 3 story w/ basement, two air handlers with a common plenum return. Return air is through a mechanical shaft w/ fire dampers on each floor. My electrical and his sub (FA contractor) want to install the duct smoke detector in the return plenum The return air for both units is CFM is 2700 each. The fact that we have fire dampers for each floor makes me a little reluctant to use return air plenum as the primary detection.
I would recommend installing it on the 2nd floor supply duct w/ remote LED/Test station w/ access door to shaft. My P.M.?s concern is that it opens up more liability such as ladder and fall arrest in the shaft.
Is the contractor off base with the return air installation?
I would recommend installing it on the 2nd floor supply duct w/ remote LED/Test station w/ access door to shaft. My P.M.?s concern is that it opens up more liability such as ladder and fall arrest in the shaft.
Is the contractor off base with the return air installation?