422.31 Motors under 1/8 horsepower - the circuit breaker can serve as the disconnecting means. That works out to 2.5 amps. Most fan coil units on split system ac units run less than that.
You are correct.. I was referencing this link:Maybe my link is faulty or my eyes are failing me, but the link to the "top secret product" shows UF wire not MC!
422.31 Motors under 1/8 horsepower - the circuit breaker can serve as the disconnecting means. That works out to 2.5 amps. Most fan coil units on split system ac units run less than that.
Its not an appliance. It is an air conditioner.
I am not in agreement with this statement. Is there an NEC stipulation that exempts air conditioners from the term appliances?
It says "UL Spec. No. 1569" on the datasheet.Where does it say it's MC cable?
I don't see it in the spec sheet
http://www.southwire.com/documents/MiniSplit_Spec_web.pdf
Where does it say it's MC cable?
I don't see it in the spec sheet
http://www.southwire.com/documents/MiniSplit_Spec_web.pdf
It says "UL Spec. No. 1569" on the datasheet.
http://ulstandardsinfonet.ul.com/scopes/scopes.asp?fn=1569.html
Cheers, Wayne
TC is not allowed in a residence unless it is in conduit. IMO, it is not the proper cable to use for this application
i agree.
Do you see any problem with the MC cable in post #28 ??
I don't see an issue with nm cable.
wow! We can't get on the same page today.
I have problem with nm as you must transition in order to run to the outside unit .
How about THIS MC cable from earlier posts. Any problem ?
http://www.southwire.com/documents/M...t_Spec_web.pdf
Sure, no problem with that MC. It is rated for DB so it should be fine but for the cost I would run NM to the outdoor area and install a Bell Box to transition to the unit. That's a lot cheaper than MC cable.
I doubt it is cheaper once you pay for the labor and material to change over to THWN.
That would depend on the distance. Last one we did was about 75' away.. IMO- nm- easier to work with in the inside unit.
Note under product description:
Tray Cable is a multi-conductor control, signal or power cable rated for 600 volts. May be installed in raceways, conduit, cable trays, and outdoor locations where supported by a messenger wire. Also suitable for direct burial. Temperature rating at 75�C wet locations / 90oC dry locations.
Kinds hides the fact that TC cable installed inside on other than industrial applications must be in a raceway (NEC 336.12)
When this product was introduced I discussed it with UL as the cur sheet I had did not identify nit as a type MC cable. UL cautioned that the product does require special connectors listed for the use.
It is slowly becoming a popular product for the mini-split installers in this area.
You do know that is just PVC Jacketed Type MC right......rebranded in what we call "lateral marketing".