1. Loss is proportional to the square of the current, so reduced losses in the lightly loaded phase wires do not offset the higher losses in the heavily loaded phase wires.
I dont follow this one can someone explain?
I'll try. But it wasn't my statement, so I might not be interpreting the comment correctly.I dont follow this one can someone explain?
Wow, so much response from a simple question, but I understand it, mostly. The 3 phases and how the relation from phase to phase varies in total output.
Anyway, one final question.
All of our loads are single phase, 120 volts. None of them are 3 phase. I checked the amps of each phase, and they are close to the same:
Phase 1 - 30.5 AMPS
Phase 2 - 46 AMPS
Phase 3 - 35.5 AMPS
I remember someone told me once this is bad and not efficient, and causes our electrical bill to go up, but I believe that is due to the inefficiency of a 3 phase motor due to un-equal load. In our case with all single phase loads, that makes no difference. Can anyone confirm or deny that?
I don't think we need to move our loads around so they are all the same, but if it would save on our electric bill, we will do it.
That's a good example of what I meant.
First, losses are equal to the resistance times the square of the current. They are even, sometimes, called "I (squared) R Losses."
Suppose you start with balanced currents of 2, 2, and 2. Each phase will have a loss that is associated with 2 (squared). So for a simple comparison, you can describe it as 4 plus 4 plus 4 (ignoring the resistance value, which we can assume is the same in all phases anyway, so it won't change the answer). That gives you a total loss that is related to the total of 12.
Now suppose you unbalance the currents, so that you get 1, 2, and 3. If you square each number, and add them, you get 1 plus 4 plus 9. That total is 14, and is higher than the original 12.
The point, I believe, is that by making one phase current higher, its losses are much bigger, because you are squaring a bigger number. At the same time, you are making one phase current smaller. But when you square the smaller number it does not have as big an impact on the overall answer.
Does that help?
It's not true.I have heard that unbalanced currents can also effect power factor is this true? If so how?
That really aint all that bad, and may even be as close as you can get. Depending on what the loads were that got added up to get each.... Anyway your bill would not change in anyway that you would notice - you would just feel better about it....All of our loads are single phase, 120 volts. None of them are 3 phase. I checked the amps of each phase, and they are close to the same:
Phase 1 - 30.5 AMPS
Phase 2 - 46 AMPS
Phase 3 - 35.5 AMPS
If the resistive load is fed with 208V, then the applied voltage is line to line, not line to neutral.Ahh... but it is.
Take for example a single resistive-only 1? 208V load on a 208Y/120 system. The current of said load will be 30? out-of-phase with the applied voltage (i.e. Line to Neutral, that of the windings), resulting in a power factor of .87. Balance that with two other identical loads and the power factor is then 1.00.
If you measure power factor using Line to Line voltage as the reference, then single phase resistive currents will have a power factor...???
Does that help?
You're right on a single phase basis, but the overall power factor will be 100%. You will have leading power factor in one phase and lagging in the other phase.Ahh... but it is.
You're using the load resistance. Load watts will be the same, balanced or not, as you have shown. What will be different is the losses. Assume conductor and transformer resistance in each phase is 1 ohm total. In the balanced case, losses will be:OK, my ignorance is showing but here goes (based on my understanding of your example):
If you have currents of 2,2,2 on the 3 phases, then each phase sees a resistance of 60 (E/I=R). I*I*R = 240. 240 + 240 + 240 = 720.
If you have currents of 1,2,3 on the 3 phases, then the R values would be 120,60,40. Using I*I*R I get loss values of 120 + 240 + 360 = 720.
This is in conflict with your statement. What did I do wrong?
Your math is OK. But you are talking about the resistance of the load. Or more precisely, your values of resistance correspond to the total resistance seen by the source. That will include the resistance of the load (the lion's share of the total resistance) plus the resistance of the wires (a small percentage). When I speak of the wires, I mean the wires that are internal to the transformer and the wires between the transformer and the load.This is in conflict with your statement. What did I do wrong?
I used Arial font instead of Times New Roman. Arial is more efficient.I have to learn to type faster, or to read the thread once more before I post, so I don't wind up posting something identical to someone who typed it faster.![]()
in⋅fi⋅nite /ˈɪnfənɪt/ Show Spelled Pronunciation [in-fuh-nit] Show IPA Pronunciation
?adjective 1. immeasurably great: an infinite capacity for forgiveness.
2. indefinitely or exceedingly great: infinite sums of money.
3. unlimited or unmeasurable in extent of space, duration of time, etc.: the infinite nature of outer space.
4. unbounded or unlimited; boundless; endless: God's infinite mercy.
5. Mathematics. a. not finite.
b. (of a set) having elements that can be put into one-to-one correspondence with a subset that is not the given set.