marmathsen
- Seattle, Washington ...ish
- Electrical Contractor
Right.OK to review the history, the 2014 NEC 210.52(A)(2)(1) reads "Any space 600 mm (2 ft) or more in width (including space measured around corners) and unbroken along the floor line by doorways and similar openings, fireplaces, and fixed cabinets." That clearly excludes walls with kitchen base cabinets from needing "wall space" receptacles.
In 2017 the sentence was changed to ". . . fixed cabinets that do not have countertops or similar work surfaces." Now walls with kitchen base cabinets with countertops are no longer exempted, and so those walls must have wall space receptacles in addition to countertop receptacles, given (2020) 210.52(A)(4) and 210.52(C).
Apparently a requirement that everyone overlooks, and likely not intended.
Cheers, Wayne
I guess what I should take away from the conversation is the intent of the code. Which if I'm understanding correctly is simply that a counter tops need receptacles where required (2-4-2), and any adjacent wall space that is 2ft or more needs a receptacle (6-12-6) but the countertop receptacles cannot fulfill that wall space requirement. No receptacles needed in the toe kick.