Well, I can say there are more than one 60 amp pullout on a water heater. I'll do some VD and thermal scans tomorrow., after I've slept well.
I been installing 60 amp pullouts for water heaters for almost 40 years. Seldom had any problems with those. I almost always used Midwest version, don't know if it is any better than the Eaton ones that were the topic of the thread or not.
 
Well they certainly don't have sufficient room for 4 AWG conductors which would be necessary if your minimum ampacity is over 55 amps @ 60C and really are not all that practical to use even with 6 AWG conductors in many cases.
IDK I have seen a melted one that I think was marked for even 3 AWG like this one;
 