That only exists if there is no substantial current flow. Under fault conditions, different parts of the system that are connected via equipment bonding conductors and equipment grounding conductors will have potential between them and often enough to be a serious shock hazard.Bonding is the connection of loose metal part to create an effective ground fault path along with a egc a SBJ (SDS) and a neutral wire back to the source. During the process of bonding these materials an equal potential is established
In post 15, that the same as what you said.I dont think thats correct
And both serve to protect equipment and people....there is no difference in their intended or actual function.Egc provide a path to source in the event oa ground fault thru the use of a egc. Thats not the only path provided to the source and the egc function is to protect equipment for the most part. Bonding is the metallical connection of loose metal thru a mechanical means. This probably provives the best route to source and its function is to protect humans. Both are part of an effective ground falt current path to source
Not correct. Bonding has to do with creating an equipotential environment; no voltage differences among parts, pieces, and eventually, peoples' bodies.
The voltage to earth, or to the source has nothing to do with it. Think about swimming-pool equipotential bonding.
Only on the equipotential part--as Don points out, that's only true when no current is flowing. If a large enough voltage is imposed across two different parts of the bonding system (EGC), then current will flow according to the resistance in between, and a voltage difference will remain.Guys, am I off the mark? Were my descriptions inaccurate?
I based that on having heard that an equipotential grid need not necessarily be connected to the equipment EGC.Has everything to do with it. What is the voltage outside of the pool relative to the ground one is standing on?
Did I misunderstand that?
That's bonding the EGC to one of the source's conductors so OCPD open before someone is shocked. Grounding the system both creates some hazards and reduces others.
Remember, it's the EGC system that begins in the service equipment, not the (now-insulated) grounded-conductor system. That's why it's okay to use a bare neutral for bonding.
GFCI equipment depends on a grounded system to function because, while earth is not conductive to energize loads, it is conductive enough to energize
Hang in there Larry. You'll get the hang of this electrical thing someday. : )Guys, am I off the mark? Were my descriptions inaccurate?
Every metallic component is a structure between the source and fault will be a current-carrying path. Your question was answered you seem to not want to believe what has been presented.This still doesnt answer my original question
Yes.Not correct. Bonding has to do with creating an equipotential environment; no voltage differences among parts, pieces, and eventually, peoples' bodies.
Here is the hardest misconception to unlearn, and the source of the OP's misunderstanding.It also serve a path back to the source which then goes to ground
Just to display my ignorance, it seems to me that bonding protects against grabbing the water line and gas line while standing on a rubber mat and getting zapped, because if properly bonded there is no potential difference between them. However, if I'm in my bare feet standing on a damp concrete basement floor, I can still get shocked (or worse). If those bonded pipes are now also grounded, as in connected to to the ground bar in the panel, then I can touch those pipes in my bare feet because the potential on the pipes should have tripped the circuit breaker, assuming something like a bolted fault. I'm not so very protected if there is a high impedance fault (say, only a few hundred milliamps) and the source is not connected to a GFCI device; I'll just get equally shocked whichever pipe I grab.![]()