I don't follow. Hasn't the entire discussion here been about modifying existing BX circuits?.
The opening post asks about receptacle replacement. One doesn't modify the armored cable, in my in-the-field experience with my AHJs, when replacing the receptacle device. I understand the question to be, is 250.118(8) including existing non-bonding strip Type AC cable? My answer is yes, and I've substantiated it with quotes from the NEC, NFPA, UL and UL's representative.