I agree the construction standard was changed, as can be demonstrated by the changes in written language of the appropriate rule of the Armored Cable article through the 1950s into the early 1960s. I have not posted quotes of this "construction rule" from the NEC, but will be happy to do so if asked.
This is where you loose me, Peter. I can't find this in the 2014 or the 2011 NEC.
2011 & 2014 NEC 250.118(8) says (in toto), "Armor of Type AC cable as provided in 320.108". 320.100 is not invoked when describing the 250.118 Types of Equipment Grounding Conductors. I have shown in direct quotes and page scans of the old NECs, posted on this Forum several times, that armored cable, installed to the NEC of its original installation, has been Type AC since the 1913 NEC went into enforcement.
The designation "Type AC" in today's NEC does not give us a way to indicate that bonding strip armored cable is the ONLY Type AC allowed as an EGC, and that non-bonding strip armored cable is not allowed as an EGC. Rule 250.118(8) calls out ONLY the "armor", it does not say "armor and bonding strip" or some variation of words that get to the meaning of the AC construction rule 320.100.