EGC Color

Most installers use bare copper in the array. (under the solar panels and between solar panels and rails)
We then transition to green type THHN, THWN-2 or similar in conduit.
250.119 requires EGC to be green when is 6 AWG or smaller. Does that indication applies even if the cable used is type PV-Wire?
 
Yes.
Who knows how it is in Costa Rica.
Costa Rica has adopted the US NEC as the electrical code. But they lack code enforcement or a building permitting system the last time I checked. So it's not uncommon to see cheaper, non-compliant, electrical work. Hence the jokes about the Costa Rica Suicide Shower.
 