ggunn
PE (Electrical), NABCEP certified
- Location
- Austin, TX, USA
- Occupation
- Consulting Electrical Engineer - Photovoltaic Systems
I am in damage control mode in a situation where a conduit was run under a concrete sidewalk for an EV charging pedestal without consulting the designer (me) on what size it needs to be, so (of course) it is too small. It's not much too small; what would make enough difference in the conduit fill would be if we could run the EGC in bare wire direct buried outside the conduit along side the sidewalk to the pedestal. Will the code allow that?