Of course, but we can't follow along at home without the details.Thanks, but so can I.
So I'm not seeing how it could end being close:Each pedestal has two 40A chargers. There is a load center in the bulding that has six 50A breakers, two each on two phases of 208V; the panel is fed by a 480/277V delta to 208/120V wye transformer.
A 40A continuous load requires a 50A breaker, and hence conductors with a minimum ampacity of 46A (since 45A is a standard breaker size). With 4 CCCs in the conduit, the ampacity adjustment factor is 0.8, meaning you need a 90C ampacity of at least 46A/0.8 = 57.5A. That rules out #8 Cu, so you'll need (4) #6 AWG Cu and (1) #10 AWG Cu EGC.
For THWN-2, #6 AWG has an area of 32.71 mm2, and #10 AWG is 13.61 mm2. That makes the total area 144.45 mm2. Per Chapter 9 Table 4, the 40% allowable area of Sch 80 PVC is 105 mm2 for 3/4", and 178 mm2 for 1".
So 3/4" is quite undersized, and 1" is plenty. What do you have?
Cheers, Wayne