I thought we had established that a conduit that contained only 120 volt control wires needed an EGC. But let me give a more specific example:
Control cabinet "A", fed by circuit 1 and associated EGC, contains a PLC, where the cabinet and PLC are connected to the EGC.
Control cabinet "B", fed by circuit 2 and associated EGC, contains a power supply and relays, and the cabinet and power supply are connected to the EGC.
A conduit routed between the two cabinets contains 10-#14 AWG, 120 volt control wires from the 120 volt output module of the PLC and are connected directly to the relays.
If the conduit is RMC, would you use this as the EGC for the control wires? Would you run a wire-type EGC with the control wires? Why or why not. NPFA 79 does not permit you to use the conduit as an EGC. Would you apply the same logic to this case?
If the conduit is non-metallic conduit, would you run a wire-type EGC with the control wires? What code section would you use to size the EGC since the control wires are not fed by an OCPD?