"equipment grounding conductors of the wire type shall not
be smaller than shown in Table 250.122, but in no case
shall they be required to be larger than the circuit conductors
supplying the equipment"
So you just want to point out that smaller is conditionally permitted?
But isn't Table 250.122 used to size EGCs based on the upstream OCPD? The point of this thread was to determined the need for, type and sizing of EGCs for control conductors not directly connected to an OCPD.