Wrong. All the normally non-current-carrying metal parts of equipment (LINE or LOAD side of the service disconnect) must have a conductive path to the grounded conductor, GEC, or both. This conductive path, by definition, is the equipment grounding conductor. If you install a jumper between any two of these parts, or from any of these parts to the grounded terminal bar, EGC, GEC, or enclosure of the service, it is an equipment bonding jumper.
I am only confused about your statements, not with the code.
I have to disagree, respectfully. Here's the simple argument to your comment. Anything grounded per Article 250
Part V Bonding uses Equipment Bonding Jumpers. Another example of an EBJ not connecting portions of EGC's is the bonding of metal piping systems and exposed structural steel as also covered under Part V Bonding, 250.104.
Grounding of normally non-current-carrying metal parts of service equipment is covered in Part V Bonding,
not in Part VI Equipment Grounding and Equipment Grounding Conductors. Additionally, you will find no mention of service, service equipment, or the such in Part VI. Yes, there is mention in Part VII Methods of Equipment Grounding... but since it's not covered in Part VI, it just adds to the confusion.
There is no requirement to provide an effective fault path on non-electrical metal parts and equipment of a building or structure that is not likely to become energized. So, if you have non-electrical equipment, it is not required to be connected to an EGC. That doesn't change the definition or purpose of an EGC. Now, if that equipment is likely to become energized, it may need to be bonded to the electrical system. Actual grounding of the equipment would be acccomplished with the use of auxiliary electrodes, which is also not required but permitted.
Grounding of the machine and cat walk, as simplistically stated, is not required. Yet as you so noted if either is likely to become energized, the cat walk would be required to be "bonded" under 250.104 (as in EBJ not connecting portions of EGC's
), while the machine would be grounded with an EGC. There are several ways to accomplish both, but I'll not get into that... unless someone feels it necessary.
The definitions, in fact, are accurate and need no clarification.
I've already stated my position and stand by it. Yet with all that said, I wish the ambiguity was removed by classifying both as simply Grounding Conductors (GC's), and then subcategorize as perhaps line side, load side, or something similar, so as to size appropriately. Also, it stands to reason if a conductor connects two or more portions of GC's, it is thence a GC...???... not this EBJ/EGC bull crap
EDIT: Just read Don's post (it wasn't there when I started my reply). I'd be happy with "BC"