crossman
Senior Member
- Location
- Southeast Texas
2008 NEC 250.148(C) Metal Boxes
"A connection shall be made between the one or more equipment grounding conductors and a metal box by means of a grounding screw that shall be used for no other purpose, equipment listed for grounding, or a listed grounding device."
Say we have a run of EMT and metal boxes with a green equipment grounding conductor pulled in it. The circuit conductors are spliced in every box. Does the green EGC wire have to be attached to each box directly at the box? Or could you just make a splice on the EGC wire in the box?
Would love to hear some thoughts. Read the section very carefully...
"A connection shall be made between the one or more equipment grounding conductors and a metal box by means of a grounding screw that shall be used for no other purpose, equipment listed for grounding, or a listed grounding device."
Say we have a run of EMT and metal boxes with a green equipment grounding conductor pulled in it. The circuit conductors are spliced in every box. Does the green EGC wire have to be attached to each box directly at the box? Or could you just make a splice on the EGC wire in the box?
Would love to hear some thoughts. Read the section very carefully...