quogueelectric
Senior Member
- Location
- new york
Not a violation the emt is a suitable ground end of story. Unless you used cast setscrew fittings of course and then you have a problem.
So... playing English Language major, note the listed items are singular. That means you can only accomplish the connection with ONE screw, [piece of] equipment, or device. Note this does not preclude the possibility of making the connection more than once, such as when each of two devices make the connection.crossman said:Okay, let's play English Language major...
"A connection shall be made between the one or more equipment grounding conductors and a metal box by means of:
1) a grounding screw that shall be used for no other purpose,
2) equipment listed for grounding,
or
3) a listed grounding device."
So...
crossman said:Okay, let's play English Language major and decipher the Code section:
2008 NEC 250.148(C) Metal Boxes - "A connection shall be made between the one or more equipment grounding conductors and a metal box by means of a grounding screw that shall be used for no other purpose, equipment listed for grounding, or a listed grounding device."
Breaking this down based on the or which I highlighted above:
There are three choices listed for grounding the box to the EGC wire. Because of the "or" used with the choices, we only have to use one of the choices to be code compliant. So the code section goes as follows:
"A connection shall be made between the one or more equipment grounding conductors and a metal box by means of:
1) a grounding screw that shall be used for no other purpose,
2) equipment listed for grounding,
or
3) a listed grounding device."
So... 2) equipment listed for grounding can be used for grounding the box. I propose that EMT and fittings are equipment listed for grounding, and the box is indeed connected to the #12 EGC wire through this listed equipment.
The #12 wire is attached to the metal panel enclosure, the box is attached to the panel enclosure via the EMT, so there ya go. I don't see that 250.148 or 250.148(C) require the connection to be made INSIDE the box.
The main part of 250.148 also involves an "or" and gives us an alternative to bonding inside the box... it allows other methods based on 250.148(C).
And the EMT meets that.
frizbeedog said:Where in this section 250.148 does it even refer to metal raceways as having anything to do with this? If were going to play english major......
This has nothing to do with type of raceway, or cable or whatever. Read not more into it than is there. Simple.
Smart $ said:So... playing English Language major, note the listed items are singular. That means you can only accomplish the connection with ONE screw, [piece of] equipment, or device. Note this does not preclude the possibility of making the connection more than once, such as when each of two devices make the connection.
frizbeedog said:If EMT meets you needs why are you running a grounding conductor? :wink:
Don't install it and you have no more problems.
crossman said:Anytime the code says "equipment grounding conductor" then we must look at 250.118 and you will indeed see that EMT is an equipment grounding conductor. So, the EMT raceway in my scenario is directly mentioned in 250.148 wherever it says equipment grounding conductor.
Agreed. TO the box. It says nothing about INSIDE the box.Pierre C Belarge said:First let me say that in your example, I would be one to say it is a violation as per 250.148 and .148(C).
Your choices 1), 2) are for the method of connecting the Grd conductors to the box.
Well, first, it is not up to the electrician to "guess-assume-play psychology of the CMP" when we read the code. The code is what it says. #2 says that "equipment listed for grounding" can complete the connection between the box and the one or more EGCs present... and it does not say the connection has to be inside the box. EMT and fittings is equipment and can be used for the purpose of connecting EGC wires to boxes, according to 250.148(C).Pierre C Belarge said:Lets remember that grounding screws are not a listed product, so they are not part of #2. That is why number 2 exists
frizbeedog said:I can't help you anymore. Good luck with that logic. Best wishes.
crossman said:Where does it say the connection has to be inside the box?
crossman said:So, everyone:
If the connection must be made inside the box, then why does the main portion of 250.148 say "within the box or to the box..."?
crossman said:Before you bail out
crossman said:However, there are plenty of instances where specs call for the EGC wire in the EMT. Also, some folks like the gold-plated redundancy of the extra wire.
So this thread could concern those installations.
frizbeedog said:Redundantly bond the wire to the box for a gold plated installation.
crossman said:I'm not saying that you shouldn't bond it if ya want. I have noticed many people assuming you have to, but you don't.
Again, if you read the sections with an open mind, and with an eye for the English language, (and you read exactly what is written, and you don't make assumptions of what was inteneded,) making note of the choices and the "ors", then you just don't have to connect the EGC wire within the box.
Thank you for the interesting dialogue so far!:smile:
frizbeedog said:.....but I'm not convinced just yet.
Just so we are clear I am on the emt is grounded bandwagon. However in reality how long and how much money would it take to put in a ground tail then slam a self grounding receptacle in with a screwgun. What are we talking 20 bucks here.crossman said:I'm not saying that you shouldn't bond it if ya want. I have noticed many people assuming you have to, but you don't.
Again, if you read the sections with an open mind, and with an eye for the English language, (and you read exactly what is written, and you don't make assumptions of what was inteneded,) making note of the choices and the "ors", then you just don't have to connect the EGC wire within the box.
Thank you for the interesting dialogue so far!:smile: