crossman
Senior Member
- Location
- Southeast Texas
iwire said:My thoughts are simply that if a wire EGC is run into a box and it's associated circuit conductors splice or terminate in that box then the wire EGC must connect to the box.
You don't get to count the EMT and it associated fittings.
Why can't you count the EMT and fittings? Can you please explain what I am missing?
It seems to me that 250.148(C) explicitly states that "equipment listed for grounding" can be used to connect EGCs to the box. If the EMT and fittings are listed for grounding, then they directly comply with the code section as a means of connecting the EGC wire to the box. EMT and fittings are equipment as evidenced in Article 100.