Is their a rule of thumb for btu's per sq. ft. for apartment electric baseboard heat? Ex. 1 bedroom apt. aprox 675 sq. ft.
Is their a rule of thumb for btu's per sq. ft. for apartment electric baseboard heat? Ex. 1 bedroom apt. aprox 675 sq. ft.
Is their a rule of thumb for btu's per sq. ft. for apartment electric baseboard heat? Ex. 1 bedroom apt. aprox 675 sq. ft.
Since ceiling heights vary, I use 1 watt per cubic foot.
No. Reason being is that this rule of thumb works in the worst case scenario. There is no penalty for short cycling of a baseboard heater. Doing a Manual J on the worst case and the average case will often yield the same heater or heaters anyhow. I use the Honeywell Line Volt Pro thermostats exclusively now. It will maintain the heat within 3/10ths of a degree. It "pulses" the heat when it starts to get close to set point, and can predicatively start pulsing the heat when it thinks it's ready for more heat. The #1 complaint about electric baseboard is the differential that all mechanical stats provide. The Honeywell Line Volt Pro makes having electric baseboard really nice.Do you apply any adjustment factors to that for things like leaky windows, uninsulated walls, etc?
Since ceiling heights vary, I use 1 watt per cubic foot.
The Honeywell Line Volt Pro makes having electric baseboard really nice.
Yes, but it's the best line voltage heating stat I've ever used. Now, it's the only one I'll use when I have any say. In much the same way that I think motion sensors are a sure-fire callback (so I only use RAB motion sensors to prevent that), line voltage stats have been a constant source of callbacks. The Honeywell Line Volt pro solves the callback problem.Looks like an Aube product that got folded into Honeywell's line when they took over Aube.
.... line voltage stats have been a constant source of callbacks.
#1 Calibration. They're notoriously off by as much as 10 degrees right out of the box. I've never installed one that was dead-nuts accurate.That's weird. What are the callback reasons?![]()
#1 Calibration. They're notoriously off by as much as 10 degrees right out of the box. I've never installed one that was dead-nuts accurate.
#2 Differential. They have differentials in the 3 to 5 degree range. That can be downright uncomfortable for many people.
In the late 60's and early 70's, an all electric home was the "in" thing. The power company would even affix a plaque next to or over the font door, proudly awarding the home the all electric seal of quality or some such thing. There's a heck of a lot of housing stock in my area served by electric baseboard heat. I've had a good many jobs the last couple years where I've replaced a failed thermostat with one of these Line Volt Pro stats, only to have them call me back to do the rest of the house. That's a super-good money maker. Hundred bucks a pop, 6 or 8 stats in a home, couple hours to change out. Good deal. You could legitimately market them as an energy saver, since they'll more accurately control the space temp and enhance the overall comfort.Around here, electric heat is generally done on the cheap for rental property, or supplemental heat. Prior to your post I've never once heard of those problems or encountered a complaint so that is an eye opener.
That's a super-good money maker. Hundred bucks a pop, 6 or 8 stats in a home, couple hours to change out. Good deal.
If you run the programs, you can see that the different parts of the country vary widely in the amount of heat needed to be supplied to any given structure.
For example, a 1250 sq. ft home built in Texas might require 63,521,600 Btu/h per hour where that same home in Mn could require 81,115,100 Btu/hour to heat.
Assuming that a 1 watt = 3412 Btu/h, the Tx home would require 18.6 Kva of heating, and the Mn home would require 23.8 Kva of heating.
The numbers are arbitrary (and admittedly low)
Then divide that by 3,412 watts (the amount of heat produced by 1-watt of electricity)
enigma-2...I believe that you need to check your math. Some of those numbers (and terms) that you use are incorrect .
steve