The specs for this customers car says in the manual it requires #6 Cu, 90 degrees with a 60 amp breaker. Romex is only rated for 60 degreesand 55 amps. I would have to run conduit with #4 all the 100 feet through this existing house. I was sure planning on romex. Boy, there goes my estimate. It is Tesla manual, she wants full power. It is very clear in the manual. Help. Do you all have to run #4 ?