Liklely it's not there as it's not required.
The requirement I believe is covered by UL 1995 is required to include an SCCR on the nameplate with the following exceptions as noted in section 37.3 :
“Equipment intended for use in one-and two-family dwellings, cord-and-attachment plug connected equipment,
or equipment supplied from a branch circuit protected at 60 A or less is not required to be marked with a short-
circuit current rating.”
I would imagine that it is based on the fact that with it is not an issue on circuits with the smaller conductor size.
For an example, a circuit using 25 ft. #6 Cu would reduce a 50,000 available fault to less than 10,000