I built my house about 4 years ago knowing that I would eventually build a boat dock so I had a 100 amp sub panel mounted on a pole in the yard close to the river. I am in the process of building a dock and needed to install a 20 amp outlet on the pole in the yard for construction. I opened the box and discovered the the sub panel has only to hot wires and a neutral, no ground wire at all. The sub now has a 30 amp double pole breaker installed to power my sprinkler system pump that is in the river. The panel inside the house has a double pole 100A breaker to power the sub. This is not a GFCI breaker. The sprinker pump is on a double pole 30A non GFCI circuit breaker. First thing is I think the sprinkler circuit should be protected by a GFCI breaker either in the main panel or the sub panel. I cannot install a GFCI breaker in the sub since there is no ground installed in the panel. What do I do?
100 amp GFCI in the main panel?
Drive a ground rod at the sub panel and use GFCI breaker in the sub.
Run a ground from the main to the sub panel. Its about 80 ft. so that may be difficult to impossible without starting over.
I have to say I am surprised that the install was approved by the elec inspector during construction.
100 amp GFCI in the main panel?
Drive a ground rod at the sub panel and use GFCI breaker in the sub.
Run a ground from the main to the sub panel. Its about 80 ft. so that may be difficult to impossible without starting over.
I have to say I am surprised that the install was approved by the elec inspector during construction.