weressl
Esteemed Member
Perhaps that does not give the inspector the authority... but I think this does:
90.7
.........
It is the intent of this
Code that factory-installed internal wiring or the construction of equipment need not be inspected at the time of installation of the equipment, except to detect alterations or damage, if the equipment has been listed by a qualified electrical testing laboratory that is recognized as having the facilities described in the preceding paragraph and that requires suitability for installation in accordance with this Code.
110.2 Approval. The conductors and equipment required or permitted by this Code shall be acceptable only if approved.
Approved. Acceptable to the authority having jurisdiction.
OK, so this would not be the first time the Code to self-contradict.