Please help me make sure this calculation is correct for a 12.9 KW range.
12.9 KW-12.0KW= .9 KW
.9KW x 5%=.o45% or 100.045%
100.045% x 8kw= 8.0036kw
8.0036kw rounds down to 8KW or 8000 W/240V = 33.3 amps
wire size # 8 thhn awg.
breaker 40amp
Thank you
12.9 KW-12.0KW= .9 KW
.9KW x 5%=.o45% or 100.045%
100.045% x 8kw= 8.0036kw
8.0036kw rounds down to 8KW or 8000 W/240V = 33.3 amps
wire size # 8 thhn awg.
breaker 40amp
Thank you