You need to install one 15A 240V or 208V circuit. It should be fed with a single 2-pole, 15A breaker.
Since it has a 15 amp plug a 15 amp circuit or 20 amp circuit will work.
Many areas around here would have you install a single receptacle so a 20 amp circuit would need a 20 amp receptacle
Doesn't a 6-15R have a T slot which will accept either a 15 or 20 amp plug?
6-15 is a twist lock, I believe.
2 Lines and a ground. No neutral.
6-15 is a twist lock, I believe.
2 Lines and a ground. No neutral.
6-15 is a straight blade 240v
L6-15 is a twistlock 240v
Doesn't a 6-15R have a T slot which will accept either a 15 or 20 amp plug?
He needs the twistlock anyway, but you have it backward. The 6-20R has the "T" to accept either 6-20P or 6-15P plugs.
Probably 2 phase. Let the debate on how proper this is begin:ashamed:What does the '2~' mean?
Probably 2 phase. Let the debate on how proper this is begin:ashamed:
I kind of assumed if it is "two pole" that what comes in one has to go out the other:blink:I think you are right. The nameplate also says '15 amps per phase'.
I kind of assumed if it is "two pole"...
Note that they did not appear to call the 240 two phase.Probably 2 phase. Let the debate on how proper this is begin:ashamed: