Is anyone fimiliar with a standard/code for wiring emergency stop or emergency shutdown circuits? Engineering at our facility is proposing to use a plc to control the e-stop circuitry, replacing the conventional hard wired circuit using a main control relay. Any help would be greatly appreciated.
Thanks
Russell
Disclaimer: NFPA 79 is not required unless adopted by your company.
See NFPA79:2007:9.2.5 Operation.
This section includes Start, Stop, Estop
See NFPA79:2007:9.4 Control Functions in the Event of Failure.
This section includes 9.4.3 Control Systems Incorporating Software and Firmware Based Controllers.
Your PLC must be listed for its usage. Safety is a special listing. Most PLCs cannot be used in safety applications.
There are safety components listed for use that are hardwired, softwired, I/O cards, and PLCs. Most vendors we work with have moved from hardwired to softwired components - Programmable Safety Relays. I am not yet seeing many move to I/O cards or PLCs.
Programmable Safety Relays include a variable number of inputs for Estops, Light Curtains, Muting, Power On/Off, etc.