rcarroll

Senior Member
700.12(D)
AHJ approved separate service. Can the separate service be supplied by the same transformer feeding the building, or, does it have to be supplied from another source? :?
Thanks
 
IMHO, I would think that 700.12(D)(2) would not allow the "emergency service" to be fed from the same transformer.

Pete
 
700.12(D)
AHJ approved separate service. Can the separate service be supplied by the same transformer feeding the building, or, does it have to be supplied from another source? :?
Thanks


Another source, if the building transformer failed you would have no emergency service.
 
I don't see anything in the code wording that would require that there be an additional transformer for an "emergency service". If that was a requirement there would be no need for the words in (D)(1) as there is no way a single service drop or service lateral could be used where there are two transformers. The key to this section is the words; "Where approved by the authority having jurisdiction"
 
The key to this section is the words; "Where approved by the authority having jurisdiction"

I think you are right, that's the key. And I would think an AHJ would be crazy to approve a second service from teh same xfrormer as an emergency service. If it were me, I would double check with the AHJ and make sure he isn't expecting services from separate transformers.
 