Hi, since I'm new, and this post will be screened (per the posting guidelines which I did read) I might not see your replies till I log on, but if you do, thank you.
We have a tenant with EHS (electromagnetic hypersensitivity syndrome. And I'm looking for ways to reduce EMFs.
Our electrician "replaced 200 amp service cable, meter socket and update grounding system" and thought this would reduce the EMFs but it hasn't. So, after this service was completed and sticker was placed tenant was still getting shocked at the kitchen sink and still reads high EMFs on the floor and walls.
Another electrical company inspected for ways to reduce EMFs and they found:
1. "Up to 1.3 amps of current was found flowing on water pipe GEC even with main breaker off suggesting a possible issue with the service neutral conductor or wiring fault. This type of current imbalance is known to cause elevated magnetic fields."
2. Some lights receive power even with main off. Therefore, there are circuits that appear to be inter-connected possibly between the two corresponding panels. This condition can lead to elevated magnetic fields."
The water company had to replace the water meter and that happened to be after the service work was done. I was reading through this post from 2008 to help with the amp on water pipe:
https://forums.mikeholt.com/threads/amps-in-the-cold-water-pipe.52016/ which made me think about the water meter maybe being the culprit for the water pipe.
I thought the service work would have corrected any issue with the service neutral conductor, and I thought the water meter would help with the shock (it might have, I don't know yet). I just don't know how to reduce the EMFs.
Any thoughts on the 1.3 amps current -- is that 'high'? (I don't know if it was amps or milliamps, sorry.)
Any experience with reducing EMFs??
Thank you so much!!
We have a tenant with EHS (electromagnetic hypersensitivity syndrome. And I'm looking for ways to reduce EMFs.
Our electrician "replaced 200 amp service cable, meter socket and update grounding system" and thought this would reduce the EMFs but it hasn't. So, after this service was completed and sticker was placed tenant was still getting shocked at the kitchen sink and still reads high EMFs on the floor and walls.
Another electrical company inspected for ways to reduce EMFs and they found:
1. "Up to 1.3 amps of current was found flowing on water pipe GEC even with main breaker off suggesting a possible issue with the service neutral conductor or wiring fault. This type of current imbalance is known to cause elevated magnetic fields."
2. Some lights receive power even with main off. Therefore, there are circuits that appear to be inter-connected possibly between the two corresponding panels. This condition can lead to elevated magnetic fields."
The water company had to replace the water meter and that happened to be after the service work was done. I was reading through this post from 2008 to help with the amp on water pipe:
https://forums.mikeholt.com/threads/amps-in-the-cold-water-pipe.52016/ which made me think about the water meter maybe being the culprit for the water pipe.
I thought the service work would have corrected any issue with the service neutral conductor, and I thought the water meter would help with the shock (it might have, I don't know yet). I just don't know how to reduce the EMFs.
Any thoughts on the 1.3 amps current -- is that 'high'? (I don't know if it was amps or milliamps, sorry.)
Any experience with reducing EMFs??