I I I I I I I just could not help myself.....
Thanks for having my back. You will be horrified to know I'm pulling less and less in branch circuit EMT.cschmid said:I I I I I I I just could not help myself.....
iwire said:It is becoming less of an issue as many boxes now have eccentric KOs that are listed for grounding.
Notable exceptions are some panel and disconnect enclosures that still use concentric KOs.
sandsnow said:I have searched, but I have not found any (none) cabinets, wireways, or pull boxes where the concentric or eccentric KO's are listed for grounding over 250 volts to ground.
I would be especially interested if anyone has seen any.
derf48 said:The heavy duty disconnects come with what is called a tangental knock out except out the back where it stills has a concentric. All tangental KO's are listed for bonding over 250 volts to ground. They have multiple points of contact with the enclosure, and you can tell the difference because they are not circular, rather are made up of multiple straight pieces, or tangents, around the circle.
Let us know what you find.RUWired said:Ok i gotta add at least something to this thread. Do the smooth locknuts on diecast connectors really dig deep enough into the paint of each enclosure to make an effective path? (never backed one off to check)
LarryFine said:Let us know what you find.