emt conduit on rooftop

Status
Not open for further replies.

Joed384

Member
Location
long island ny
I need to run a 200 amp 480 volt panel feeder across a rooftop of a commercial building. Is 3" EMT with compression couplings on conduit rooftop supports acceptable as per NEC. How about sch 80 as an option as well? Thanks for any imput.
 
EMT requires fittings listed for wet locations not just standard compression fittings.
 
Didnt realize there was a difference for comp vs wet location fittings. Thanks, that could have been bad.

How about this. EMT out of buliding to a GRC 90 then convert to the PVC sch 80 across the roof.
 
Didnt realize there was a difference for comp vs wet location fittings. Thanks, that could have been bad.

How about this. EMT out of buliding to a GRC 90 then convert to the PVC sch 80 across the roof.
They will say wet on them, might have a gasket, some brands are color coded. I see schedule 80 mentioned often, never used it. What about schedule 40?
 
Im not a fan of sloppy looking work, So maybe the best option (Cost and quality) would be the EMT option from end to end with the wet location fittings.

I would just run the EMT and use XHHW so you can forget about any derating. :)
 
"XHHW in a wet location has a maximum operating temperature of 75c according to the UL White Book, 310.15(B)(16) and 310.104. So, ampacity correction begins with the 75c ampacity due to the wet location"
Copied
 
"XHHW in a wet location has a maximum operating temperature of 75c according to the UL White Book, 310.15(B)(16) and 310.104. So, ampacity correction begins with the 75c ampacity due to the wet location"
Copied

Two points

XHHW-2 is what I find for sale

XHHW-2 will not require roof top derating.
 