Can you buy the connector with two locknuts or they only come with one? Thanks.
Can you buy the connector with two locknuts or they only come with one? Thanks.
Spec calls for it. It's security system conduits. Why couldn't you do it by design? Looks like it'll fit on threadsBy design, your desire doesn't make sense. You couldn't screw two locknuts on an EMT connector, nor would you even need two.
Spec calls for it. It's security system conduits. Why couldn't you do it by design? Looks like it'll fit on threads
Sent from my SM-N960U using Tapatalk
Are they actually asking for conduit or tubing?Spec calls for it. It's security system conduits. Why couldn't you do it by design? Looks like it'll fit on threads
Sent from my SM-N960U using Tapatalk
Two locknuts and the metal of a box won't fit on any EMT connector I have ever seen.
Conduit EMT they want ..isn't that tubing . I know what you meant thoughAre they actually asking for conduit or tubing?
Roger
So they specifically call out EMT? What is the actual wording of the spec?Conduit EMT they want ..isn't that tubing . I know what you meant though
Sent from my SM-N960U using Tapatalk
Spec calls for it. It's security system conduits. Why couldn't you do it by design? Looks like it'll fit on threads
Sent from my SM-N960U using Tapatalk
ThanksWhat are they trying to accomplish with the second lock nut? A properly installed lock nut shouldn't vibrate loose ( it is designed to dig into the metal of the box). If that's their concern I would think that a locking compound on the threads would serve better (not needed).
Spec calls for it. It's security system conduits. Why couldn't you do it by design? Looks like it'll fit on threads
Sent from my SM-N960U using Tapatalk
EMT is not conduit. If they are asking for conduit you would not be able to use EMT.
Spec calls for it. It's security system conduits. Why couldn't you do it by design? Looks like it'll fit on threads
Sent from my SM-N960U using Tapatalk
EMT is not conduit. If they are asking for conduit you would not be able to use EMT.
I agree with you from a technically correct position, however, as an estimator I have seen EMT referred to as conduit more often than not. For example, "All wiring shall be in conduit." Then specifying EMT in walls, PVC under slab, etc. or even 3-3/0, #6G in 2" EMT Cond. on a feeder. So, I wouldn't dwell on that technicality.
But we do that so well.......
I agree with you from a technically correct position, however, as an estimator I have seen EMT referred to as conduit more often than not. For example, "All wiring shall be in conduit." Then specifying EMT in walls, PVC under slab, etc. or even 3-3/0, #6G in 2" EMT Cond. on a feeder. So, I wouldn't dwell on that technicality.
Here you go. From a job I am working. Took me less than 5 minutes.I can't ever recall having seen EMT referred to as conduit in a spec.
I have seen where specs say something like "unless otherwise noted, all conduit shall be in rigid...", and then having some places in the spec where it will allow for other kinds of raceways in certain cases like using PVC UG.