10Driver
- California
- Retired
OK, just came across a situation that I think needs to be corrected. Have a solar system that is properly grounded from the PV's to the inverter (have two inverters). The Inverter case is plastic and the EMT has a grounding bushing connecting the EMT to a ground bus bar in the inverter. However, from the inverter a ground wire goes from the inverter through the FMC to a combiner MLO (connecting the two inverters) but there's no ground bushing on the FMC (leading from the plastic inverter case to the metal combiner) attached to the inverter bus bar on one end nor is there a grounding bushing at the combiner MLO to the combiner MLO ground bus bar (which has concentric knockouts). The ground IN the FMC does connect to the inverter ground bus bar at one end and the combiner bus bar at the other end BUT if I'm reading 250.64(E)(1), the FMC with a ground wire INSIDE needs to be grounded ON BOTH ENDS....
I think the FMC needs to be grounded on both ends through approved methods. Any thoughts????