Ktdidone
New member
- St. Louis, Mo, USA
Can EMT be "fished" in walls?
I think you meant installed in the walls. It will be hard to fish in the walls, but not impossible.
358.30 Securing and Supporting. EMT shall be installed
as a complete system in accordance with 300.18 and shall
be securely fastened in place and supported in accordance
with 358.30(A) and (B).
(A) Securely Fastened. EMT shall be securely fastened in
place at least every 3 m (10 ft). In addition, each EMT run
between termination points shall be securely fastened within
900 mm (3 ft) of each outlet box, junction box, device box,
cabinet, conduit body, or other tubing termination.
Exception No. 1: Fastening of unbroken lengths shall be
permitted to be increased to a distance of 1.5 m (5 ft) where
structural members do not readily permit fastening within
900 mm (3 ft).
Exception No. 2: For concealed work in finished buildings
or prefinished wall panels where such securing is impracticable,
unbroken lengths (without coupling) of EMT shall
be permitted to be fished.
2014 NEC 358.30(A) exception #2.....unbroken lengths (without couplings) of EMT shall be permitted to be fished.
It can be fished, but might be tough.
Um, if the wall is more than 20 feet tall, what did you do, use an EMT stretcher?Exception No. 2: For concealed work in finished buildings
Forgive me, but who would ever know there was a coupling down the wall? I know, I know, I'm a baaaaddddd boy![]()
Sent from my SM-G935P using Tapatalk