jwelectric said:
Just so there is no misunderstanding about what I am saying let me be perfectly clear. There is no code language nor is there anything in the UL White Book that makes a statement that a RMC coupling can not be used to transition from one raceway to the other.
All this hype about it being a violation of UL listing is nothing more than hype and no one will convince me other wise without something in writing that I can read for myself.
I believe that you are adding words to my statement of making some sort of assumption without all the facts.
What I am saying is if the uses of a RMC coupling to make a transition from one raceway to another is wrong then simply show me where it states that it is wrong.
I think that I have been through this many times before but will do it again if necessary. UL Standards has nothing to do with the installation of electrical equipment. The instructions that are included with the listing and labeling process and the NEC is what the installer goes by when making an installation.
UL Standards is what the manufacturer of electrical equipment has to follow in the manufacturing process. The NEC and the White Book is what electricians use to make the installations.
In the UL White Book on page 100 and 101 it gives the listing of raceway fittings. The last sentence of the first paragraph states:
All fittings are intended to be installed in accordance with ANSI/NFPA 70 ?National Electrical Code? (NEC), and are intended for installation and use in accordance with the following information and the limitations specified in the appropriate conduit or tubing category.
Nowhere in the entirety of Conduit Fittings (DWTT) of the UL White Book do I find a limitation on the use of a RMC coupling as outlined in this thread. Any thing else is nothing more than plain old hog wash and has no merit to stand on.
I don't have a copy of the white book in front of me, but are there any limitations of other types of fittings outlined in the book? For example, is there anything that would prevent me from using a setscrew coupling in a meyers hub? What about a compression fitting with a rigid conduit body? The combinations are endless and I am sure that the standards don't address every one. I am sure that the UL White Book doesn't say that you CAN use the RMC in that specific application. It plain doesn't define anything except the standard methods.
As for UL Standards, they are consensus based documents which are developed by:
? Manufacturers, which use the standards to design products and systems that meet requirements for certification;
? Regulatory authorities, which reference the standards for products and systems used in their jurisdictions;
? Code development organizations, such as the National Fire Protection Association and International Code Council, and government agencies, such as the Occupational Safety and Health Administration, which adopt and reference UL safety standards; and
? Certification organizations, which apply UL requirements for product evaluations.
While these UL standards may have little to do with the actual installation of the product, they sure do take into account how it is installed when the standards are developed.
You obviously have not had an inspection resulting in an issue with the installation that you are discussing. However, in other jurisdictions, I am sure that it is treated differently, no matter how you interpret the codes.
I ask you, if the application (or combination of fittings) thereof is not mentioned in any UL listing, does it still mean it's ok? It's certainly not my place to say, as the AHJ has the final say per Art 100.
It's obvious that we have separate opinions, and I respect you for that. So...let's agree to disagree...ok? :smile: