TOOL_5150
Senior Member
- Location
- bay area, ca
If this is a violation, please explain UL listed semi-flush all-in-one's & metercans that are so common here in CA.
See my post above.
~Matt
If this is a violation, please explain UL listed semi-flush all-in-one's & metercans that are so common here in CA.
Now that would be interesting. :grin:
Now to be a royal pain in the behind, I submit the position that the referenced Code Section refers to the Disconnecting Means, and not necessarily the riser or the conductors within per se.
The main argument to support the issue is whether or not the conductors contained within the riser are considered as "within the building" by being in an exterior wall cavity. :grin:
Looking at my 1999 NEC (latest book I have on hand right now) Sec. 230-6 defines the conditions which make the conductors defined as "outside the Building" which includes the following:
(2) "Where installed within a building or other structure in a raceway that is encased in concrete or brick not less than 2 in. (50.8mm) thick."
So unless the raceway is encased in concrete or brick not less than 2" thick then it would be considered as "inside the building." Reasonable enough.
But here's the kicker: After reading the entire Section for services 600v nominal or less, nowhere in that Section 230 is a prohibition of Service Conductors inside the building.
In fact , Section 230-52 says the following: "Where individual open conductors enter a building or other structure, they shall enter through roof bushings or through the wall in an upward slant through individual, noncombustible, non absorbent insulating tubes. Drip loops shall be formed on the conductors before they enter the tubes."
Again, this is from the 1999 book I have right now, and I concede that there is perhaps another Section that spells out the prohibition or that later Code cycles did indeed change that Section.
So next reference please. :grin:
Not worth my time, the section is clear, I understand CA allows it, the NEC does not.
http://www.youtube.com/watch?v=39f2pd4y8Ac&feature=relatedNow Bob, don't be grumpy. :grin:
There is NOTHING in the entire section 230 that states in any way that service conductors are prohibited inside the building. In fact they allow open conductors according to that Section.
I do agree with your statement and reference on the service disconnect, but we're talking about the riser not the disco.
This makes me wonder where this whole thought process comes from..I recall that there were discussions on this forum in regards to "what does the nearest practical point for the disconnect mean in terms of length of conductors allowed inside the building" as the Code did not specify a hard distance.
I maintain that a riser inside a wall is NOT a Code violation and most certainly is not the huge fire hazard that some may think it is.
As for theft of service issues brought up by TOOL_5150, that is a POCO problem and design issue not enforceable by the NEC.
If there is any other Section/Article that prohibits the riser in the wall then I'd love to know of it, as would my AHJ friend.
Now Bob, don't be grumpy. :grin:
There is NOTHING in the entire section 230 that states in any way that service conductors are prohibited inside the building.
In fact they allow open conductors according to that Section.
I do agree with your statement and reference on the service disconnect, but we're talking about the riser not the disco.
I maintain that a riser inside a wall is NOT a Code violation and most certainly is not the huge fire hazard that some may think it is.
If there is any other Section/Article that prohibits the riser in the wall then I'd love to know of it, as would my AHJ friend.
No, I do not do work at the airport. Please read my post again:
"We are not alowed to run it in the wall any more. If its a service upgrade and its in the wall, it has to be put on the outside and a new roof jack installed, overhead service of course. I fully agree with this code. It makes sence for the safety and protection of theft of service. As far as the newer underground services, they are in the wall in the garage usually."
~Matt
Well surprise, I live and work in the Bay Area, and we ARE allowed to put service risers INSIDE the wall for overhead services. The only limitation is that RGS is used. What city is not allowing it ?
Somehow, all the electrical manufacturers (GE, Murray, CH, Square D) must have screwy business plans, because they all make semi-flush panels that can only be installed with the riser in the wall. Someone please explain this fact for me.
The fact items are manufactured has nothing to do with the item being used code compliantly. To me that is like saying a NEMA 1 box can be used in any location just because it is manufactured and listed.
With the semi flush service panel the inspector could make you concrete encase the riser etc.
The fact items are manufactured has nothing to do with the item being used code compliantly. To me that is like saying a NEMA 1 box can be used in any location just because it is manufactured and listed.
With the semi flush service panel the inspector could make you concrete encase the riser etc.
Well surprise, I live and work in the Bay Area, and we ARE allowed to put service risers INSIDE the wall for overhead services. The only limitation is that RGS is used. What city is not allowing it ?
I have no idea where you are getting this from but PG&E definitely allows overhead services. I have and installed many of them this year. PG&E would prefer you stay with overhead services if the distribution in the area is overhead. They charge a premium for underground services in overhead areas. PG&E allows flush mounted panels for both overhead and underground services. Its pretty hard to install an underground panel flush unless you fir the wall out to allow for the minimum 3" raceway. Structural engineers are disallowing semi-flush panels on many projects since they don't want the hole cut into their sheer wall. Some local jurisdictions such as Woodside and Portola valley want all new service to be underground but that has nothing to do with PG&E.PG&E does not allow OH services any more - unless you are in an area that only has OH service, which, really, who the hell is building right now - especially in older neighborhoods.
every time I have pulled a permit to swap out an OH service, PG&E said that the mast/riser has to be outside the building. Which I think is stupid, because all new homes are built with the UG riser IN the [usually garage] wall.
But in all reality, just dealing with PG&E is hit or miss, Ive been told from different employees that i can do my own disconnects and reconnects to I cannot, and if I do I will recieve a huge fine. :roll: I hate that company.
~Matt
As a manufacturer, who makes non-listed LFMC (a product that has been required to be listed since the 1996 code), explained to me one day when I asked about the product...there is no violation in selling the product...the violation only comes when you install it....
Somehow, all the electrical manufacturers (GE, Murray, CH, Square D) must have screwy business plans, because they all make semi-flush panels that can only be installed with the riser in the wall. Someone please explain this fact for me.
I agree that the NEC does not permit this installation but it has been standard practice in CA for many years. The funny part is we are not allowed to run exposed SE cable that most of the country accepts.
Weather PG&E actually does allow it, or not, in certain cities or not - it is against code. I use surface mounted panels on all my OH service upgrades.
~Matt
I would LOVE to see someone suggest a proposal to specifically ban service risers in wall and see what happens. I won't do it because I don't agree with the position that it is/should be prohibited.