A home-owner tapped the line and put in a relay system that would drop the tapped load when the meter was pulled.
No, I have never thought of doing that. :grin:
A home-owner tapped the line and put in a relay system that would drop the tapped load when the meter was pulled.
You really caught me at a bad time because if there was a stress ball in front of me I would crush it.
So be prepared for blunt answers. :grin:
YOU ARE WRONG! (Blunt huh)
230.70.(A)(1) prohibits service conductors inside the building.
230.70(A)(1) requires the disconnecting means to be nearest the point of entrance. Once the conductors reach the disconnecting means they are no longer service conductors they are feeders and can run as far as you want.
Up to the disconecting means which is required to be where the SCs enter the building.
It makes no difference
Ok you have a "riser" that goes into a meter which has conductors that connect to the line side of the meter can. The meter and riser are not the service disconnect. The load side of the meter conductors go to a service disconnect. I don't see 230.70 (a) violation.
Ok you have a "riser" that goes into a meter which has conductors that connect to the line side of the meter can. The meter and riser are not the service disconnect. The load side of the meter conductors go to a service disconnect. I don't see 230.70 (a) violation.
We had a case in Georgia where the service ran through the attic ahead of the meter. A home-owner tapped the line and put in a relay system that would drop the tapped load when the meter was pulled. It was not found until the house was sold and the new owner wanted to know what the contraption in the attic was for. As you might imagine, drops through attics are frowned upon now-a-days.
...
Good, and since CA is a leader, you must do as we do or we will boycott you. You see the lesson we've taught AZ. :grin:
Most, but not all:But I think most us agree that they can enter the building. If so, the only words we can play with are "inside", and "nearest".
...YOU ARE WRONG! (Blunt huh)
230.70.(A)(1) prohibits service conductors inside the building...
...So 230.70(A)(1) while not specifically stating a length prohibits service conductors from running lets say 'unrestricted' in the building.
He thought it would work the same as one of the DIY ice-maker kits you get for the fridge.We've seen one of those too, but this guy was only drilling a hole with a 1/4 inch bit. How was he going to tie into the service drop?
Maybe no horror but just a widdle bit scawy: :grin:Please point out the 'horror stories' that 'some are making it out to be'.
All I have said is it ridiculous to think that unused service conductors in a wall are as safe as outside the building.
No horror stories, no smoldering wreckage.
You really caught me at a bad time because if there was a stress ball in front of me I would crush it....
It is both a code violation and a hazard...
Now I have to go beat a wall until I break a hand.
I am stupefied that you think I can run service conductors an unlimited distance inside a structure without complying with 230.6 I am literally shocked that you of all people do not see any hazard in doing so.
That I would agree with. How long has that section been in place because I have seen a bunch of it in old locations?In this case the riser from weatherhead to combination semi flush meter socket panel board is inside the wall. That is IMO a direct violation of 230.70(A)(1).
That I would agree with. How long has that section been in place because I have seen a bunch of it in old locations?
No problem for me. I'm worse on a bad day, but I'm happy at the moment.mivey, at least put the correct posts together if you are going to post my superposed responses to them. :roll:
And as far as horror stories I still see none.
I see a guy that was a bit to up front about his day, sorry if that was a problem for you.
I only have back to 1978 (my newbie days) where it was in the grouping section 230.72(c) and said basically the same thing as the current code.Interesting, as far as I knew that has been the topic of this thread all along.
mivey, at least put the correct posts together if you are going to post my superposed responses to them. :roll:
And as far as horror stories I still see none.
I see a guy that was a bit to up front about his day, sorry if that was a problem for you.
Volta, Precisely because there seems to be no agreement that the riser is technically inside the building.
220.12 Lighting Load for Specified Occupancies.
A unit load of not less than that specified in Table 220.12 for occupancies specified therein shall constitute the minimum lighting load. The floor area for each floor shall be calculated from the outside dimensions of the building, dwelling unit, or other area involved. For dwelling units, the calculated floor area shall not include open porches, garages, or unused or unfinished spaces not adaptable for future use.
In this case the riser from weatherhead to combination semi flush meter socket panel board is inside the wall. That is IMO a direct violation of 230.70(A)(1).
Article 220 has already defined what the inside building space consists of and inside of a wall cavity is within the building
If the building was only considered within the interior walls it would be stated.
Roger
Main Entry: 1in?side
Pronunciation: \(ˌ)in-ˈsīd, ˈin-ˌ\
Function: noun
Date: 14th century
1 a : an interior or internal part or place : the part within b : inward nature, thoughts, or feeling c : viscera, entrails —usually used in plural
2 : an inner side or surface
3 a : a position of power, trust, or familiarity <only someone on the inside could have told> b : confidential information <has the inside on what happened at the convention>
4 : the area nearest a specified or implied point of reference: as a : the side of home plate nearest the batter b : the middle portion of a playing area c : the area near or underneath the basket in basketball
Roger said:If the building was only considered within the interior walls it would be stated.
New Art 100 entry said:Inside. For the purposes of enforcing this Code, inside shall be considered as all areas and locations on the interior side of building exterior walls and finishes. Wall cavities shall for the purposes of this Code be considered inside.
Since the Code doesn't say that (yet) I call a riser as being outside.