Thanks for the reply. My "long form" is similar to the one in Annex J. What I am trying to develop is a permit that would be issued to a qualifed employee and be vaild for 6 months. This "standing permit" would allow them to perform routine tasks. In our case that would be anything less then 600 volts and 400 amps or less. Because it is not refering to a specific task almost everything listed in Annex J doesn't apply. I'm thinking it will be more of a statment that the employee understands our policys, they will use the appropriate PPE ect.
Be careful with standing permits, they need to be task specific. <600V and <400A means nothing, that could be all types of different tasks and different hazard levels, the <400A part scares me, the load has little to do with the arc flash hazards and shows a lack of understanding, unless I am misuderstanding your intent.
Most of the tasks will wind up being under LOTO except for trouble shooting.
Our policy is to NEVER work on anything energized. The only exception is for testing and troubleshooting.
testing and troubleshooting does not require an energized electrical work permit.
Can you please site a reference. 130.1 seems to say otherwise.
130.1 (B)(3) Exemptions to work permit - "testing, t/s, and voltage measurements shall be permitted to be performed without an EEWP.."
Seems pretty clear to me.
I would be leery of anything that lasts for 6 months.
I took this idea of a "standing permit" from an article in EC&M. They indicate that a standing permit can be valid for one year for routine tasks.
since a permit is not required for the most common things done while energized, just what other routine tasks would it cover?