LarryFine
Master Electrician Electric Contractor Richmond VA
- Location
- Henrico County, VA
- Occupation
- Electrical Contractor
Yes, if the inside panel contains the service disconnect, by all means perform the neutral/ground bonding, but you should not parallel the neutral with a second conductor.Hmm, that’s not how we usually do it
but I am used to NYC inspections and not this upstate jurisdiction. I like your solution, however. I will bond everything in the service cabinet also.
The electrode conductor may attach to the neutral at any (one) point. The meter base is actually ideal, since it's outdoors, but we're not allowed to land ours there in Virginia.