Hi all:
I have read through many of the previous posts on this but can't seem to get an answer to my questions...or, enough answers for me to form a picture of how I'm going to do this correctly.
This is going to be my first hot tub connect for a client who is installing an above ground hot tub on a pad that he built. The pad is, from what I have seen/been told, a 6" high box (4'X4' PT) with non-reinforced (no rebar - unknown depth) pilings spaced in it, packed with sand - pavers on top. The pad will be about 1' larger in diameter than the tub.
Here is what I'm proposing based on 2011 NEC/ Sec 680:
Spa is requiring a 120/240V 50A GFCI protected ckt.
- Run #8/4 (if I can get it - a cable w/ an insulated ground) from panel in garage through crawlspace, pop out through sill plate into a disconnect (10' away from spa - within sight). LFMC over to the tub.
- Bury a #8 bare solid CU 6" deep around the tub just on the outside edge of the pad (or within a few inches) - bonding it to the gnd bar in the pump housing (provided there is space/accomodations). Does this need to be a complete ring? That is, connected like a lasso and then run up into the ground bar? If I can't make a bond in the pump housing I guess I'll run it back to the disconnect?
- I have written to the company to see if the hot tub has provisions for bonding the water. If not, what could I do? Connect a coffee can to a wire and drop it in the tub?:thumbsdown: What have you other guys done if there aren't provisions for doing this?
Lastly, provide a service receptacle on a separate ckt. located by disconnect.
Hopefully, I have painted a clear enough picture so that you might see if I'm missing something here. Again, I have read many variations for installations in previous posts (I.E. ring -vs- grid EPB, cable sized at continuous -vs- noncontinuous duty, etc....not much on the bonding of the water.
Thanks for your input...
Scott
I have read through many of the previous posts on this but can't seem to get an answer to my questions...or, enough answers for me to form a picture of how I'm going to do this correctly.
This is going to be my first hot tub connect for a client who is installing an above ground hot tub on a pad that he built. The pad is, from what I have seen/been told, a 6" high box (4'X4' PT) with non-reinforced (no rebar - unknown depth) pilings spaced in it, packed with sand - pavers on top. The pad will be about 1' larger in diameter than the tub.
Here is what I'm proposing based on 2011 NEC/ Sec 680:
Spa is requiring a 120/240V 50A GFCI protected ckt.
- Run #8/4 (if I can get it - a cable w/ an insulated ground) from panel in garage through crawlspace, pop out through sill plate into a disconnect (10' away from spa - within sight). LFMC over to the tub.
- Bury a #8 bare solid CU 6" deep around the tub just on the outside edge of the pad (or within a few inches) - bonding it to the gnd bar in the pump housing (provided there is space/accomodations). Does this need to be a complete ring? That is, connected like a lasso and then run up into the ground bar? If I can't make a bond in the pump housing I guess I'll run it back to the disconnect?
- I have written to the company to see if the hot tub has provisions for bonding the water. If not, what could I do? Connect a coffee can to a wire and drop it in the tub?:thumbsdown: What have you other guys done if there aren't provisions for doing this?
Lastly, provide a service receptacle on a separate ckt. located by disconnect.
Hopefully, I have painted a clear enough picture so that you might see if I'm missing something here. Again, I have read many variations for installations in previous posts (I.E. ring -vs- grid EPB, cable sized at continuous -vs- noncontinuous duty, etc....not much on the bonding of the water.
Thanks for your input...