If the size of the bare ground the manufacturer uses in the SER is based on 3 phase with the bare being the neutral...how do they pick this #3 size? Other than the neutral cannot be smaller than the EGC and must be sized handle the unbalanced load, I don't see any requirements. It may not be always be appropriate to have #3 neutral with #1 conductors I would think. The GEC minimum for AL 1/0 or small is #6. I'm trying to understand pro/con running SER (1/1/1/3) or CU conductors in EMT. If I use CU, I can use #3 for hot legs, #8 Ground, #8 Neutral (if load is well balanced or #6 to be safer). Added benefit is harder to put a nail through EMT than SER. I am always more on cautious side but also don't want to be wasteful.