Why do you want to tie an EGC to the gutter?
EPB is it's own network. Any items in that network that also require an EGC, pool pumps or lights are just some common examples, is where an interconnection to the EGC typically comes into play.
typically for bodies of water, the bond grid gets tied to the egc at some point. so if a gutter is in the bond zone and you already had a egc wire running up to the gutter via some hidden path (wall, attic, roof rafter, etc) and tied to the gutter, the gutter then becomes part of the bond grid via egc. thus, if the grid near the pool became 500v, then so should the gutter and everything else that the egc lands on. so instead of a 500v "circle" you now have a bunch of 500v fingers.
a bond grid is great if you are in the middle of it, not so great if you are at the edge of it.
in the case of a fully isolated bond grid (not tied to egc), if the bonding gets energized by another ckt that perhaps does not have gfi, there is no egc on the grid to clear that fault and you end up with a potential shock hazard near the edge of the bond grid, like grid to earth, or grid to something else that is tied to egc, etc.
isolation is "bad" for pool scenarios. the grid should be good, tied to egc (perhaps in more than one place, like pump and disco/sub), and tied to a few ground rods.
perhaps NEC should simplify the 680 section, just call it an extended egc grid.