You are not accounting twice. If a 40 amp load is continuous then 210.19 is saying the minimum ampacity of conductor you use must be 125% of 40.Thanks Wayne. That's the answer I've been given most often- that you are supposed to intertwine the two tests together. I just can't find where the Code says to do that. It also seems like doing so contradicts the definition of allowable ampacity, which says already clarifies that it's talking about a continuous circuit.
You can account for the circuit being continuous by reducing the ampacity of the cable (40a actual current =< 40a adjusted ampacity) or increasing the current of the load (50a calculated current =< 50a actual capacity), but why would you account for it twice?
210.20 says basically the same thing but applies to overcurrent protection instead of conductor ampacity.
Somewhere in art 240 the two are also tied together because the conductor must be protected at no more than it's rated ampacity.
The allowance for higher overcurrent goes through 240.3 and on to other sections mentioned there. Things like motors, AC and refrigeration, capacitors, etc. though those all still typically require 125% of actual load for minimum conductor ampacity.