Fred B
Senior Member
- Location
- Upstate, NY
- Occupation
- Electrician
Other than the fact Romex (NM-B) is only allowed to be at the 60oC rating thus #8 only good for 40A.
Every EVSE that I've installed (3 different brands I deal with) all had wire sizing listed with the equipment indicating for the 40-48A to use min. size 90 deg wire of #6AWG, protected by a 50A or 60A breaker. Those 2 factors would mean no NM or UF or any 75 Deg wiring, per mfg. specs.
Every EVSE that I've installed (3 different brands I deal with) all had wire sizing listed with the equipment indicating for the 40-48A to use min. size 90 deg wire of #6AWG, protected by a 50A or 60A breaker. Those 2 factors would mean no NM or UF or any 75 Deg wiring, per mfg. specs.