EV Charger: #8 Romex on 50a Breaker

Fred B

Senior Member
Location
Upstate, NY
Occupation
Electrician
Other than the fact Romex (NM-B) is only allowed to be at the 60oC rating thus #8 only good for 40A.
Every EVSE that I've installed (3 different brands I deal with) all had wire sizing listed with the equipment indicating for the 40-48A to use min. size 90 deg wire of #6AWG, protected by a 50A or 60A breaker. Those 2 factors would mean no NM or UF or any 75 Deg wiring, per mfg. specs.
 

retirede

Senior Member
Location
Illinois
Other than the fact Romex (NM-B) is only allowed to be at the 60oC rating thus #8 only good for 40A.
Every EVSE that I've installed (3 different brands I deal with) all had wire sizing listed with the equipment indicating for the 40-48A to use min. size 90 deg wire of #6AWG, protected by a 50A or 60A breaker. Those 2 factors would mean no NM or UF or any 75 Deg wiring, per mfg. specs.

Are those hard-wired EVSEs?

It would seem very strange for them to dictate the type of wire used if the unit connects with a cord and plug. As long as the mating receptacle is installed in compliance with the NEC, it should be sufficient.
 

Fred B

Senior Member
Location
Upstate, NY
Occupation
Electrician
Are those hard-wired EVSEs?

It would seem very strange for them to dictate the type of wire used if the unit connects with a cord and plug. As long as the mating receptacle is installed in compliance with the NEC, it should be sufficient.
Hard wired, I won't do receptacle, had issues with GFCI - charger conflicts and nuisance tripping.
 

curt swartz

Electrical Contractor - San Jose, CA
Location
San Jose, CA
Occupation
Electrical Contractor
There is no issue running a 50 amp circuit with #6 NM-B for a 40 amp charger. A 48 amp charger requiring a 60 amp circuit would require #4 NM-B.

NM-B has 90C conductors but the ampacity is limited to that of 60C conductors.
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
How did it come about that the 60C NM limitation was removed from SE cable about 10 years ago?
I believe some testing was done in 2009-2010 around attic temperatures and cables a report got published. That got SE cable that is installed in thermal insulation de-rated for the 2011 NEC.
then later more testing of SE cable revealed its XHHW insulation larger than 10 AWG is fine in thermal insulation so the need to de-rate was removed from the 2017 NEC
My supply house lists 8 Cu SER in the catalog, but it is not in stock - have to order 1000 feet.
How much is 1000' reel?
 

Birken Vogt

Senior Member
Location
Grass Valley, Ca
8/8/8gnd Cu SEU 1.73 no stock, don't know what they would say if tried to order
6/6/10gnd NMB 2.24 in stock by the foot
4/4/4/8gnd NMB 6.91 in stock by the foot - 4/2 not available
6/6/8gnd SEU 2.29 not in this region but others seem to be selling by the foot
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
8/8/8gnd Cu SEU 1.73 no stock, don't know what they would say if tried to order
That 8/3 SER seems like a good investment, between hi-end ranges that recomend a '50 amp circuit' and EV chargers I bet its worth us stocking a spool, I am going to look into that. The other option would be a some of that tray cable thats now listed for Joist pull.
 

Birken Vogt

Senior Member
Location
Grass Valley, Ca
That is 8/2 SER with bare ground. From the illustration it looks like a round stranded ground but it is not always accurate. Might be concentric.

I was just typing out all the conductors found in the cable to be precise there.
 