EV Charger: #8 Romex on 50a Breaker
Other than the fact Romex (NM-B) is only allowed to be at the 60oC rating thus #8 only good for 40A.
Every EVSE that I've installed (3 different brands I deal with) all had wire sizing listed with the equipment indicating for the 40-48A to use min. size 90 deg wire of #6AWG, protected by a 50A or 60A breaker. Those 2 factors would mean no NM or UF or any 75 Deg wiring, per mfg. specs.
Are those hard-wired EVSEs?
It would seem very strange for them to dictate the type of wire used if the unit connects with a cord and plug. As long as the mating receptacle is installed in compliance with the NEC, it should be sufficient.
Hard wired, I won't do receptacle, had issues with GFCI - charger conflicts and nuisance tripping.
How did it come about that the 60C NM limitation was removed from SE cable about 10 years ago?
I believe some testing was done in 2009-2010 around attic temperatures and cables a report got published. That got SE cable that is installed in thermal insulation de-rated for the 2011 NEC.
then later more testing of SE cable revealed its XHHW insulation larger than 10 AWG is fine in thermal insulation so the need to de-rate was removed from the 2017 NEC
My supply house lists 8 Cu SER in the catalog, but it is not in stock - have to order 1000 feet.
How much is 1000' reel?
8/8/8gnd Cu SEU 1.73 no stock, don't know what they would say if tried to order
6/6/10gnd NMB 2.24 in stock by the foot
4/4/4/8gnd NMB 6.91 in stock by the foot - 4/2 not available
6/6/8gnd SEU 2.29 not in this region but others seem to be selling by the foot
That 8/3 SER seems like a good investment, between hi-end ranges that recomend a '50 amp circuit' and EV chargers I bet its worth us stocking a spool, I am going to look into that. The other option would be a some of that tray cable thats now listed for Joist pull.
That is 8/2 SER with bare ground. From the illustration it looks like a round stranded ground but it is not always accurate. Might be concentric.
I was just typing out all the conductors found in the cable to be precise there.