wwhitney
- Berkeley, CA
- Retired
Conservative but not tight. For identical 2-wire loads of X amps, delta connected arranged as balanced as possible, then the magnitude of the line currents (A,B,C) will be:Is correct?
(1) (X,X,0)
(2) (X, sqrt(3) X, X)
(3) (sqrt(3) X, sqrt(3) X, sqrt(3) X)
(4) (sqrt(4+sqrt(3)) X, sqrt(4 + sqrt(3))X, sqrt(3) X)
(5) (sqrt(4+sqrt(3)) X, 2 sqrt(3) X, sqrt(4+sqrt(3)) X)
(6) (2sqrt(3) X, 2 sqrt(3) X, 2 sqrt(3) X)
(7) (sqrt(12+sqrt(3))X, sqrt(12+sqrt(3))X, 2 sqrt(3) X)
So if you're using, say 40A EVSEs (which need 50A branch circuits), 4 of them would give a required transformer rating of 40 * sqrt(4 + sqrt(3)) * 208V * sqrt(3) = 34,500 VA. Versus 40 * 208 * 3 = 24,960 VA for 2 or 3 EVSEs, and twice that for 5 or 6 EVSEs.
Cheers, Wayne