Hey guys, I’m an electrical contractor and I specialize in residential EVSE installation. The grace period in New Jersey is over in a few days so we will be on the 2020 NEC which means GFCI protection of EVSE. I have a few questions that I would appreciate help from the code experts.
Most of my installations are either a 50 amp receptacle or hardwired with a 50 amp or 60 amp circuit.
My understanding is that a 50 amp receptacle needs to be GFCI protected whether it’s inside of the garage or outside of the house.
And a hardwired EVSE needs to be GFCI protected only when outside of the house, not when in the garage. Is that correct? Because I’m also reading that a 60 amp hardwire doesn’t need to be GFCI protected no matter where it is, so I’m a bit confused.
I also just want to confirmation that I can use a spa panel (hot tub GFCI disconnect) installed next to the load center to GFCI protect this circuit since some GFCI breakers could be either hard to find or extremely expensive?
Most of my installations are either a 50 amp receptacle or hardwired with a 50 amp or 60 amp circuit.
My understanding is that a 50 amp receptacle needs to be GFCI protected whether it’s inside of the garage or outside of the house.
And a hardwired EVSE needs to be GFCI protected only when outside of the house, not when in the garage. Is that correct? Because I’m also reading that a 60 amp hardwire doesn’t need to be GFCI protected no matter where it is, so I’m a bit confused.
I also just want to confirmation that I can use a spa panel (hot tub GFCI disconnect) installed next to the load center to GFCI protect this circuit since some GFCI breakers could be either hard to find or extremely expensive?