Sounds like a trick question. One could say 110.12(A) would not allow a plastic KO seal in a metal box.
I believe a NM seal is allowed in a metal box. 110.12(A) indicates:Where metallic plugs or plates are used with nonmetallic enclosures, they shall be recessed at least 6 mm (1/ 4 in.) from the outer surface of the enclosure.Sounds like a trick question. One could say 110.12(A) would not allow a plastic KO seal in a metal box.
I believe a NM seal is allowed in a metal box. 110.12(A) indicates:Where metallic plugs or plates are used with nonmetallic enclosures, they shall be recessed at least 6 mm (1/ 4 in.) from the outer surface of the enclosure.
Whose question is this, or who's asking it? Could you post the question exactly as written?
When using a NM KO plug in a metal box how far does it stick into the box? This is a question I could not come up with an answer from the NEC. 110.12A describes the opposite of what Im looking for. Any help would be appreciated!!
110.12(a) says metallic plugs or plates with nonmetallic enclosures, it doesn't mention nonmetallic plugs with metallic enclosures.
these should be fine on metallic enclosures.
View attachment 6774