we are doing a project where they want to reuse exisitng 2x4 laying fixtures T8. The fixtures had been 277 now the new circuit for lighting is 120v and the fixtures are missing the small J box cover with green screw that is normally on fixture. I have a 2 part question

first Can I supplement the J box cover with a fabricated cover and 1/2'' knockout and ground screw and still be cover under NEC and UL listing of fixture ? I was thinking of screwing a handy box cover with 1/2'' ko they self tapping a ground scew, what you think is this OK?

Second Since the ballast was already tapped at 277 will the 120v ballast take to new voltage, I keeo hearing it wont work. I am going to try tomorrow and see if it does But I will give no guarantee they will stay on. Also these fixtures are in ware house with OS sensor. Is there a specific ballast i should be using for this application any way to work with OS, like a rapid start ? The fixtures are pretty old and not sure what is already mounted I will check morning
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
It will depend on the specific ballast being used.

See this old thread:
http://forums.mikeholt.com/showthread.php?t=137797

Some ballasts adjust for the supply voltage, other apparently 'blow' (somehow?) the unused feed when used at one or the other voltage.

-Jon
If you put fuses in each tap, then in theory the higher current through the low voltage tap could blow that fuse. But that would imply that the various inductor "taps" would actually have to be separate coils without mutual inductance to avoid shorting out energized turns by paralleling them.

Modern electronics could make the same choice reversibly.

mobile
 

solis

Member
My experience has been newer multi-volt ballasts don't have a "memory", the ballast will adjust to the supply voltage within the range of the ballast, older ballasts, 10+ years, can have an issue sometimes.
 

kwired

Electron manager
Location
NE Nebraska
In general you can't use self tapping screws for EGCs.
You can use a self tapping screw that utilizes "machine screw" type of threads. I believe there must be a minimum number of threads engaged into the metal, which is why you sometimes must use the raised bump that has a hole for a grounding screw in it - the metal is thick enough there to comply.

From recollection anything less then 32 threads per inch is not acceptable in 1/16" or less of metal, which would be two threads must be engaged in 1/16 of an inch. A nut on the back side however would be acceptable if not enough threads are engaged.

What you generally can't use is "sheet metal" variety of screws
 

jumper

Senior Member
You can use a self tapping screw that utilizes "machine screw" type of threads. I believe there must be a minimum number of threads engaged into the metal, which is why you sometimes must use the raised bump that has a hole for a grounding screw in it - the metal is thick enough there to comply.

Two threads.

250.8(A)

(5) Machine screw-type fasteners that engage not less than
two threads or are secured with a nut
(6) Thread-forming machine screws that engage not less
than two threads in the enclosure
 

kwired

Electron manager
Location
NE Nebraska
Note that you cannot use a nut instead of two threads with a self-tapping screw.

mobile
I will only say that there are machine thread screws that can tap their own threads and there are non machine thread screws that tap their own threads. There are also screws of both types that can drill their own hole before tapping threads.

Most of the 10-32 "ground screws" I have purchased for several years need a previously drilled hole, but can tap threads in that hole if there is none.
 

iwire

Moderator
Staff member
Location
Massachusetts
You can use a self tapping screw that utilizes "machine screw" type of threads. I believe there must be a minimum number of threads engaged into the metal, which is why you sometimes must use the raised bump that has a hole for a grounding screw in it - the metal is thick enough there to comply.

From recollection anything less then 32 threads per inch is not acceptable in 1/16" or less of metal, which would be two threads must be engaged in 1/16 of an inch. A nut on the back side however would be acceptable if not enough threads are engaged.

What you generally can't use is "sheet metal" variety of screws

I stand by what I said.
 

iwire

Moderator
Staff member
Location
Massachusetts
And I can see your definition of "self tapping screw" to be the primary reason. I don't hold that against you:)

I don't have any problem with my definitions or understanding of the code section.


Perhaps you have problem understanding what 'generally' means?

With all that you have said a handy box cover is to thin to tap threads into and be code compliant so thanks for the trip to nowhere. :D
 

kwired

Electron manager
Location
NE Nebraska
I don't have any problem with my definitions or understanding of the code section.


Perhaps you have problem understanding what 'generally' means?

With all that you have said a handy box cover is to thin to tap threads into and be code compliant so thanks for the trip to nowhere. :D

I can't recall ever attaching a grounding screw to a handibox cover, but thanks for the that information if it should ever come up.:)
 

K8MHZ

Senior Member
Location
Michigan. It's a beautiful peninsula, I've looked
Occupation
Electrician
Could these be used? I know they are a PITA, but they are a compliant means to attach a ground conductor without worrying about threads.

GC.jpg
 

Electric-Light

Senior Member
Nobody mentioned this, but it will draw 2.3 times the current. Is the branch sized generously enough that at 2.3 times, it stays under 80% rule?

I've never seen documented statement that 120-277v ballasts lock out, but that above would be a reason they might do so. Just depending on how loaded it was on 277v, running on 120v can leave the wiring at varying degree of overload.
 
Last edited:

Holop

Member
Location
Seattle
I believe ground screw needs to be listed for such means. Example I've seen retrofit can light is supplied with a zinc green color tek screw included with the kit. It's kinda catch 22 because inspectors themselves don't know about this and almost always require documents for the screw or retro can light.