if a C1D1 rated motor leads are "POTTED", does this mean it is sealed and can be used in a C1D1 location?
Thanks.
do you need an EY seal fitting then?
A capacitor start motor would have a contact to open the start capacitor circuit, but could still be sealed and require no additional sealing. One needs to look at motor information to know for certain.I don't think I have ever used an EY when connecting to a C1D1 motor.
They aren't an arcing device and I don't think one is required.
I'd like to see the catalog cut.The motor does not say if it is factory sealed but the catalog sheet says the leads are potted.
So does potted means it is sealed?
I'd like to see the catalog cut.
"Potted" basically means "contained"; as in a potential explosion would be contained in the motor enclosure. It isn't commonly used, but it isn't improper either. I'm more concerned that there isn't a nameplate or label on the motor enclosure indicating it is factory sealed.I cannot remember ever seeing that word used on an XP motor.
I have seen it on motors intended to be submerged though.
but it is not like I have looked real closely at XP motor spec sheets all that much.
ETA: So I went and looked at a Baldor XP motor cut sheet. Guess what? It uses the word "potted" to describe the seal between the junction box and the motor.
You can indeed see the "potting" easily enough, but can you tell visually if it is sufficient for a factory seal.You can usually see the seal inside the p-head of the motor.
You can indeed see the "potting" easily enough, but can you tell visually if it is sufficient for a factory seal.
So why would you believe it is? As I mentioned to tkb above, while you can see the "potting", can you tell if it is a sufficient seal without a manufacturer's marked certification?pics of the nameplates on the peckerhead and the motor. no indication it is factory sealed.
also the catalog sheet shared by our colleague is the cat. sheet for the motor we are using.
thanks.