....it will just take an electrician to remedy it.
Definitely an inspector chosing the 'my way or no way' mentality.
Why, can't the siding be moved away?
....it will just take an electrician to remedy it.
Electrical inspector sees only electrical solution, perhaps?Definitely an inspector chosing the 'my way or no way' mentality.
Why, can't the siding be moved away?
Definitely an inspector chosing the 'my way or no way' mentality.
Why, can't the siding be moved away?
The fact that you can work on it is not the point.
It is 'closed in' per the definition that I posted.
" not permanently closed in by the structure
or finish of the building."
"Closed in" and "recessed" are completely different configurations.
The NEC is written very carefully. (Although we all still find much to debate about!!)
If the code you referenced meant recessed, it would say recessed.
Not trolling. If I thought this was an acceptable installation I would put my contractor hat on and try to argue my point.
True and TY. I do have one on my side. The AHJ who was there and witnessed this first hand.
"Set back" is what I am using.
:slaphead: Yes, "set-back" is what you are using, but unfortunately for your side of the debate, the code you referenced says nothing about "set-back"
Again this is not an electrician's problem it will just take an electrician to remedy it.
My main concern is that the original installation was modified. The kind of stuff we see when they take a light off then screw it though the siding to connect to the box. You all have seen it.
But the OP said that they were re-working the wiring.
It just seems that as each code violation you reference gets shot down you reach for another straw.
I think everyone on the other side of this debate will agree that the result of the addition of the insulation and the siding has made a PITA situation for anyone who will work on it, but that is not enough to make it a code violation.
No he did not.
The original post was an open ended question.
Then the OP made the comment that he would 'tear off the siding and extend the box, like it should have been in the first place'. There was no mention of what the owner wanted done.
A little later, the OP posted the state inspector said 'no way - extend the box', but still no NEC reference was provided.
Mike, you haven't posted a relevant code section yet, you just keep grasping for straws and posting irrelevant code sections that you want (with a stretch of the imagination) to fit your cause and dislike of the situation.I was never "shot down". One violation was not enough so I listed others.
I have not called him ignorant. But I do not know what reference he is using, you are assuming it is the same as yours.Other than calling him ignorant/wrong
I have not called him ignorant. But I do not know what reference he is using, you are assuming it is the same as yours.
I have consistently asked you how far you want the siding moved so that you would approve the installation.
I would ask the same question of the 'state inspector'.
Nope, it is not closed in by any stretch of the imagination.Accessible (as applied to wiring methods). Capable of
being removed or exposed without damaging the building
structure or finish or not permanently closed in by the structure
or finish of the building.
Appears to be closed in. Fails.
So now since grasping for other code sections got shot down you want us to believe that the receptacle shown is over 600 volts. Just admit that you can not come up with a code suported reason to fail it and just say you are standing your ground on the "I don't like it" argument.110.31
(C) Outdoor Installations.
Does not apply.
110.32 Work Space About Equipment. Sufficient space shall be provided and maintained about electrical equipment to permit ready and safe operation and maintenance of such equipment. Where energized parts are exposed, the minimum clear work space shall be not less than 2.0 m (61?2 ft) high (measured vertically from the floor or platform) or not less than 914 mm (3 ft) wide (measured parallel to the equipment). The depth shall be as required
in 110.34(A). In all cases, the work space shall permit at least a 90 degree opening of doors or hinged panels.
Does not apply.
Nope, it is not closed in by any stretch of the imagination.
So now since grasping for other code sections got shot down you want us to believe that the receptacle shown is over 600 volts. Just admit that you can not come up with a code suported reason to fail it and just say you are standing your ground on the "I don't like it" argument.
Roger
You continuously show sections that don't apply, your reference to Part III of 110 is just another example. How does over 600 volts come in to play here?Grasping? Showing you sections that do not apply?
If others tried to use the same article sections they would be just a s wrong.ust show what others might use and does not apply.
I think he was using the "I don't Like It" reason as well.I didn't get shot down - the Inspector that actually inspected this came to the same conclusion.
Ahah, so now it comes out, a couple of inspectors on pedastals make an "I don't like it" call and they can not be wrong because they are so far above us. Are you sure you want to stay with that statement in this arena?I'd say that the AHJ agreeing with me is all that need be said. That's telling a judge he is wrong. Doesn't matter a decision was made.
Once again, we don't have to cite a code section that allows anything, you as the inspector have to cite a violation, and you haven't done it succesfully in this discussion.I played along and gave you measurements. Now show me what allows an installation to be modified to limit it's access!
You want me to take him 110.32 first?
Can this question be answered?
For this Outlet to be considered accessible and in compliance the NEC , the siding,"Blockout",or surrounding wall covering aound the existing outlet must be kept _______________ inches away from each side, and ____________ inches away from the top and bottom of the existing code compiant outlet, per NEC Code ________________________________.
NO. Confirmed by AHJ.
For this Outlet to be considered accessible and in compliance the NEC , the siding,"Blockout",or surrounding wall covering aound the existing outlet must be kept _____3__________ inches away from each side, and _____3_______ inches away from the top and bottom of the existing code compiant outlet, per NEC Code ____90.4 Enforcement*____________________________.
*By special permission, the authority having jurisdiction
may waive specific requirements in this Code or permit
alternative methods where it is assured that equivalent objectives
can be achieved by establishing and maintaining
effective safety.
At what depth of recess (or as you call it - permanently closed in) would this apply? 1/16th", 3/4", 1 1/4", 3" ?
How far can I now recess and be acceptable with the above specified blocked out area? 3", 6", 18"?
NEC does not really give us a thorough definition of just how easy it must be to access in the definition of accessible. There are junction boxes in crawl spaces (that must be accessible) that maybe 25 years ago I could fit into the space to access, but today I may not be able to get there. Code violation?OK let's start with why it failed. Access. I could not hold the cover up with my left hand and insert my tester with my right hand.
View attachment 9640
As I stated earlier it is the contractors responsibility to address this on the plans. As an Inspector (if I was involved) I cannot (legally, I am not a plans examiner) give you a solution. If this was (OP) approved on the plans then it passes. I would express my thoughts on why it should not have been approved to the AHJ but it is not my call.
I'll play plans examiner. First I would look at:
Accessible, Readily (Readily Accessible). Capable of being
reached quickly for operation, renewal, or inspections
without requiring those to whom ready access is requisite
to climb over or remove obstacles or to resort to portable
ladders, and so forth.
Passes.
Accessible (as applied to wiring methods). Capable of
being removed or exposed without damaging the building
structure or finish or not permanently closed in by the structure
or finish of the building.
Appears to be closed in. Fails.
I know you are a better code guru than that, it was even pointed out that those sections apply to over 600 volt and you ignored that in replies that followed.110.31
(C) Outdoor Installations.
Does not apply.
110.32 Work Space About Equipment. Sufficient space shall be provided and maintained about electrical equipment to permit ready and safe operation and maintenance of such equipment. Where energized parts are exposed, the minimum clear work space shall be not less than 2.0 m (61?2 ft) high (measured vertically from the floor or platform) or not less than 914 mm (3 ft) wide (measured parallel to the equipment). The depth shall be as required
in 110.34(A). In all cases, the work space shall permit at least a 90 degree opening of doors or hinged panels.
Does not apply.
Not every job in every location goes through plans review. I have never taken part in any such plans review, I have had an informal reviewing with an inspector when encountering something a little out of the ordinary just to make sure we are both on the same page before even commencing work. I think you mentioned in a later post you can not legally give a contractor a solution, I find that a little hard to entirely believe. It probably comes down to how you present it. If you tell them "this is how you are going to do it" that is probably a solution, if you tell them "here is one way that will work" it is only a suggestion. Don't tell me that when you do write up correction notices that a possible solution isn't right there in the violation description sometimes.If the contractor showed me on the prints a 8" X 8" or 12" X 12" total area for the 'outlet' I would probably approve it. Depending on it's depth. How deep can this outlet be set back?
It is the contractor's responsibility to have this taken care of before an inspector arrives.
I too as an EC could probably change the receptacle but being talented does not make it accessible.
We shot down the other inspector also, but at the same time he has not been feeding us input on why he failed it, how do you know he wouldn't have taken information from this thread and changed his mind if he were a participant here?Grasping? Showing you sections that do not apply? Just show what others might use and does not apply.
I didn't get shot down - the Inspector that actually inspected this came to the same conclusion.
I'd say that the AHJ agreeing with me is all that need be said. That's telling a judge he is wrong. Doesn't matter a decision was made.
I played along and gave you measurements. Now show me what allows an installation to be modified to limit it's access!